[Prev][Next][Index][Thread]
RE: Transformer Proctection Circuits?
- 
To: tesla@pupman.com 
 
- 
Subject: RE: Transformer Proctection Circuits? 
 
- 
From: Terry Fritz <twftesla@uswest.net> 
 
- 
Date: Thu, 10 Feb 2000 07:09:35 -0700 
 
- 
Approved: twftesla@uswest.net 
 
- 
Delivered-To: fixup-tesla@pupman.com@fixme 
 
- 
In-Reply-To: <NCBBLNLHCJEMOCIKJCJDEEMNCCAA.parn@fgm.com> 
 
- 
References: <4.1.20000119202327.00a3faf0@pop.dnvr.uswest.net> 
 
At 07:38 AM 02/10/2000 -0500, you wrote:
>
snip....
>> 	Option (3) is my favorite.  It gives good high frequency 
>> attenuation and
>> the caps referenced to ground help insure that the secondaries 
>> cannot float
>> to a great voltage.  I also use MOVs and spark gaps in the protection
>> filter.  I have a string of 1800V  2500A MOVs from each secondary leg to
>> ground.  On the spark gap side of the protection filter, I have a 
>> spark gap
>> with each leg referenced to ground.  With this filter and MMC caps,
>> secondary to primary strikes should be fully protected against.  I do not
>> use strike rails.
>> 
>> Cheers,
>> 
>> 	Terry
>
>Hi Terry,
>
>Do you by any chance have a diagram on the web I can take a
>look at showing your protection circuitry?
>
>Many Thanks,
>Bill
>
Hi Bill,
See the following.  Not that the values may change depending on your NST
and such.  The resistors should dissipate about 5-10% of the system power.
http://users.better.org/tfritz/newcoil/newcoil.gif
http://users.better.org/tfritz/newcoil/19.jpg
http://users.better.org/tfritz/newcoil/115.jpg
http://users.better.org/tfritz/newcoil/116.jpg
Cheers,
	Terry